Är det någon som har provat att sätta trådbundna IR detektorer på ingångarna?
Vad gäller för spänning på ingången?
Title: Re: IR detektorer på ingångar
Post by: Jan (Microbit) on 2013-07-12, 08:49:36
Detta gäller för ingångarna enligt infot på www.webswitch.se:

There are two digital inputs which can be used in the Auto Control Programs. For both of them the inactive mode is “High” and the active mode is “Low”. Inactive mode is when the screw terminal connection “IN-1″/ “IN-2″ is left unconnected to “0V”.  Active mode is achieved by connecting them to the the “0V” terminal which is located between them. No voltage should therefore be applied to them.